Rail Module Communication Fault
hijazih
Post by hijazih »
When turning on the EST Panel for the first time one of the troubles being noticed is
" 01070601 Rail Module Communication Fault"
at 0107**** location the component is 3-ASU.
it is being noticed also that the all the LEDs of the ASU in on all the time.
Thanks for any suggested idea..
phongred
Re: Rail Module Communication Fault
Post by phongred »
i have same problem, i change new CPU, it ok
FireTech
Post by FireTech »
When you see all the Leds flashing or pulsating, that is an indicator that it is in "Comm Fail" Hence... The " 01070601 Rail Module Communication Fault" you are getting..
-- Make sure you have the Cables on correctly between your Chassis. (and seated firmly)
-- Look at your SDU program. What do you have programmed for Rail #2? And, Have you Compiled/Coverted and Loaded your CPU in question?
-- All due respect... You have some troubleshooting to do before you are close to replacing the 3-Cpu.
delanil
Post by delanil »
Panel :est3
Status: Panel shows rail module communication fault after download.
Earlier Panel was working fine
Please suggest a solution.
Thanks for any suggested idea..[/quote]
briac
Post by briac »
delanil ,
I have the same problem but it desapear like this few seconds or minute after,
I thinks te rail module is busy during the download,
try to reduce the baud at 19200 maximum,
Do not rush the download,do it slowly;
check the RX and TX LED on each module and you will see which one is not responding.
thanks,