maintenance alert on ZB16 zone

Post Reply
anthony08
Posts: 11
Joined: Thu Apr 07, 2011 11:57 pm

maintenance alert on ZB16 zone

Post by anthony08 »

hello,
There is a "maintenance alert" in in one of zone of ZB16- we cleaned all the detector connected to this zone still the "maintenance alert" message is displayed, I remove the smoke detector wire from zone then install the eol-resistor, restarted the control panel, after a few minutes, the "maintenance alert" returned

Is this a sign of defective ZB16 card?

thanks
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: maintenance alert on ZB16 zone

Post by Leo »

it is most likely not the ZB16 that is giving you the maintenance alert
the maintenance alert is coming from the SLC loop its one of the siga smokes
run reports on ALL your SLC loops/SDDC cards, 20% and 80%
Fireworks
Posts: 12
Joined: Sat Oct 01, 2011 12:04 pm

Re: maintenance alert on ZB16 zone

Post by Fireworks »

Had the maintenance alert a few times on different panels that came from the ZB16 card.
It would happen during verifications where your putting a panel/circuit through things it would
normally not be doing.
Never really tried to figure out why it happened, maybe high impedance on the circuit, just my guess.
A piece of programming code that was never fully implemented or documented, but still exist.
I have never replaced a board because of this, just powered it down for a minute and it was fine after that.
anthony08
Posts: 11
Joined: Thu Apr 07, 2011 11:57 pm

Re: maintenance alert on ZB16 zone

Post by anthony08 »

thanks guys,
But we already replaced the zb16 card, this solved the problem