Posts: 9
Joined: Sun Sep 16, 2012 12:02 pm

est 3 network

Post by calebking »

hi

can anyone help with a 32 est3 panel network. a few years ago the panles would drop off-line then lock up and had to be restarted. we scoped the panels and changed a few repeaters and netwoek cards. we also found the earth wasnt in A-class. so we re-cabled the whole network in 2.5mm shielded copper cable and bounded the earth at 1 panel and left floating around the rest. this worked and system stayed clear for a year but lately has returned. the panles all drop of line the restore straight away but network is unstable. any help would be great

cheers

john
briac
Posts: 93
Joined: Sat Jul 28, 2012 10:16 am
Location: GMT+3

Re: est 3 network

Post by briac »

good day,
please check first the lengh of the cable then the routing mode, check also if there is a power cable or gamma ,X ray influence around your system network,
the made ​​to weaken it may be due to the installation instructions,the cable is gray if the glass is exposed to heat humidity and may be moisture
FireTech
Posts: 80
Joined: Wed Dec 24, 2008 9:44 am

Re: est 3 network

Post by FireTech »

I used to be a "Site Tech" for an Est3 network that was 30-40 Nodes. Question..... If you look at the History or Print out after one of these "Panel Drop Outs" , does it start with the same Node number?
Also.... Here is what you Look at:
1-) Is 485 cards "seated" properly behind CPU? Is the White nylon screw installed in EVERY 485 card?
2-) Do you have any panels that have a long distance between them? If yes, How Far Apprx?