Sounder Base

Post Reply
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: Sounder Base

Post by Leo »

one of two things the CR has been activated or you are wired to the N/C connect.
riztgh
Posts: 11
Joined: Sat Oct 15, 2016 2:58 am

Re: Sounder Base

Post by riztgh »

Thanks Leo,
Can you help me with Rules so that sounder base only activates when the particular detector in alarm.
Old fire alarm guy
Posts: 6
Joined: Mon Feb 08, 2016 6:57 am

Re: Sounder Base

Post by Old fire alarm guy »

Here's some rules from a job I did in NYC for the combo CO & smoke detectors:

[SMOKE ALARM LOOP 3A 3-5]
ALARM SMOKE 'COSMK_LOOP_3A_*_<N:1-83>' : ON 'TCDR_CH1_LOOP_3A',
ON 'COSMK_LOOP_3A_*_<N>';
[SMOKE ADA ALARM LOOP 3A RM402]
ALARM SMOKE 'COSMK_LOOP_3A_<N:26>_*' : ON -LOW 'STRB_L8_RM402';

[SMOKE ADA ALARM LOOP 3A RM404]
ALARM SMOKE 'COSMK_LOOP_3A_<N:27,28>_*' : ON -LOW 'STRB_L8_RM404';

[SMOKE ADA ALARM LOOP 3A RM502]
ALARM SMOKE 'COSMK_LOOP_3A_<N:59>_*' : ON -LOW 'STRB_L9_RM502';


[CO SOUNDER LOOP 3A 3-5]
COSUPERVISORY 'COSMK_LOOP_3A_*_<N:1-83>' : ON 'TCDR_CH2_LOOP_3A',
ON 'CO_TO_CO',
ON 'COSMK_LOOP_3A_*_<N>';
riztgh
Posts: 11
Joined: Sat Oct 15, 2016 2:58 am

Sounder Base

Post by riztgh »

Hi All,
For sounder bases , we use siga-CR wiring with all sounder base in a floor and ends with 47kohm EOL just like the wiring diagram given in AB4G datasheet. But, when we switch on the power switch, the all sounder bases starts ringing without any alarm. The sounder base will sounds when the smoke detectors experience smoke. Can anyone please help me with rules...
Post Reply