Rule & device Type for siga-CT2

Post Reply
briac
Posts: 93
Joined: Sat Jul 28, 2012 10:16 am
Location: GMT+3

Re: Rule & device Type for siga-CT2

Post by briac »

Hi,
put the CT 2 on alarm (pull for example) when you enter the device during panel configuration.
then on the table of the panel config change the PULL on the second serial number to SUPERVISORY. and that's all.
note that the terminal 7 and 8 are the first serial number and has to be set on alarm.

hope to help you.
khorasani
Posts: 37
Joined: Fri Sep 19, 2014 9:25 am

Rule & device Type for siga-CT2

Post by khorasani »

Hi everybody,
I have connected a door contact(NO) and a trouble contact of ASD(Air Sampling Detector) to a siga-ct2 module.now i want to determine device type for siga-ct2 in 3-SDU and write a rule for it;so that when the door closed ,an audible device go to alarm .and when I have a fault from ASD have a trouble message on LCD of EST3 panel .
any one can help me please?
many thanks.