Simplex - alarm verification tally limit exceeded

Post by Leo »

Simplex "alarm verification tally limit exceeded"

To clear this trouble you will need to login with a Level-4 login
without a level-4 login it can not be Cleared!
this is a pseudo point 214
once login with a level-4
hit the 7 which has a P on it then 214
pseudo point P214 will display as "Abnormal"
hit the on/arm then off/disarm key
hopefully this will clear the trouble
now do a warm restart, the panel is in service mode and needs to be warm restarted
via menu->panel restart->warm restart
in the menu goto warm restart [enter] [enter]
DONE