Edwards Signaling - FireShield - F-Dact FSdact programming
GE Security Fire & Life Safety F-DACT(F) Digital Alarm Communicator Transmitter Installation Sheet
http://www.edwards-signals.com/ E-FSC Series F-DACT Dual Line Dialer, E-FS
E-FSC Series Conventional Fire Alarm Control Panels -> http://www.edwards-signals.com/?pid=405"
page 45 -> attached: 3101175_R03_FSC_Series_Technical_Reference_Manual.pdf
5 Programming buttons:
Reset - Scroll
Remote Disconnect - advance to the next program option.
Panel Silence - save and advance to the next digit
Walk Test - previous
Signal Silence - previous setting for the current option
passcode: Default: 1111111
To get started:
1. Install program jumper PRG. Panel common LEDs flash and the panel enters a trouble state. The trouble buzzer sounds.
2. Press Remote Disconnect to advance to the first programming option (Load Defaults). The LEDs stop flashing, the Disable LED (binary 1) lights, and Load Defaults is displayed on the LCD. The trouble buzzer turns off; however, the panel is still in a trouble state.
3. Do not load defaults. Press Walk Test until “DACT Programming” is displayed.
4. Press Reset until Yes is selected.
5. Press Panel Silence to begin FSDACT programming. The panel automatically switches to FSDACT programming mode and “DACT Programming” is displayed on the LCD.
6. Enter your password. Refer to “Programming the FSDACT” below.
Note: You can exit from programming mode at any time by removing the program
Programming the FSDACT
When you program the FSDACT, you’ll follow these general
steps:
1. Enter your passcode
2. Load default settings
3. Edit your passcode
4. Enter the date
5. Enter the time
6. Select the FSDACT mode
7. Enter the (DACR1) primary phone number
8. Enter the (DACR1) secondary phone number
9. Enter the (DACR1) account code
10. Select the DACR1 alarm format
11. Select the restore option for CMS one
12. Enter retry count one
13. Enter retry time one
14. Enter the (DACR2) primary phone number
15. Enter the (DACR2) secondary phone number
16. Enter the (DACR2) account code
17. Select the DACR2 alarm format
18. Select the restore option for CMS two
19. Enter retry count two
20. Enter retry time two
21. Select tone or pulse dialing
22. Select AC fail delay time
23. Enter the transmission test time
24. Select the transmission test frequency
25. Enter the number of rings to answer
26. Select the ring type
27. Enable (disable) call back
28. Enter the call back phone number
Tip: If you save an incorrect digit, press Walk Test then Remote Disconnect. This returns the cursor to the first digit.
Press Panel Silence until the cursor is at the incorrect digit.
Enter the correct digit, then press Panel Silence to save and advance to the next digit.
docs - P/N 3100353
Edwards FireShield - F-Dact FSdact programming
Edwards FireShield - F-Dact FSdact programming
- Attachments
-
- FireShield 3, 5 and 10 Zone Installation Manual.pdf
- (1.61 MiB) Downloaded 656 times
-
- 3101175_R03_FSC_Series_Technical_Reference_Manual.pdf
- (1.19 MiB) Downloaded 573 times