some problem regarding est-3 network card rs485
-
- Posts: 15
- Joined: Tue Feb 15, 2011 8:08 am
Re: some problem regarding est-3 network card rs485
Describe the problem, what is happening, I have not had a specific issue but I have had problems with high power two-way radios
Re: some problem regarding est-3 network card rs485
the issue is..when there is sudden surge on power supply like diesel power generator its damaging the network card..why not the power supply?
-
- Posts: 15
- Joined: Tue Feb 15, 2011 8:08 am
Re: some problem regarding est-3 network card rs485
Does the 485 card go completly bad or does the network just go down and come back up. Must be an old generator because we have several building with backup diesel generators and if they are wiping out panel parts then the generator has some major issues. The reason for the first question is because it may be more of an EMF issue depending on how the network cabel is ran.
Re: some problem regarding est-3 network card rs485
it sounds like an EMF thing, is the network cable shielded?
almost always it's because we used shielded cable that we had a problem, I know they say use shielded cable to stop EMF but it sames to be the opposite.
If you are using shielded cable ground only one end.
- try a surge protector designed for a rs485 line, it works great the stop lighting problems.( both ends )
almost always it's because we used shielded cable that we had a problem, I know they say use shielded cable to stop EMF but it sames to be the opposite.
If you are using shielded cable ground only one end.
- try a surge protector designed for a rs485 line, it works great the stop lighting problems.( both ends )
Re: some problem regarding est-3 network card rs485
yes the card was fried up..the network cable is shielded and is free from earth fault..i think this is the weakest part of the est-3 panel..
Re: some problem regarding est-3 network card rs485
one end of a shielded cable needs to be grounded.
If a shielded cable is not installed right it will be a bigger problem then if non-shielded cable was used.
I would look into the shield and play with that.
If a shielded cable is not installed right it will be a bigger problem then if non-shielded cable was used.
I would look into the shield and play with that.
-
- Posts: 15
- Joined: Tue Feb 15, 2011 8:08 am
Re: some problem regarding est-3 network card rs485
A cable shield problem would cause communication issues however a completly burned up fried 485 card means there is something wronge in the field. At this stage in the game it would be best to run a temp cable on the ground and do several simulated tests this will help eliminate EMF/Field wire as the Problem
Re: some problem regarding est-3 network card rs485
well im talking about a mall having a 43 est-3 panel..pulling a temporary cable i guess is not a good option..has anyone tried here fixing an isolator module on the network?
Re: some problem regarding est-3 network card rs485
how many times has this happen?
It maybe a lightning problem, shielding makes lightning problems worse.
I would think about lightning suppression, the few times I have used they it has made a bad problem just disappear.
get the right type (data rs422/485) its a low voltage type.
If this is that big of a problem I would just put them, at least at the worse panels.
and if it is not lightning it still may fix the problem.
It maybe a lightning problem, shielding makes lightning problems worse.
I would think about lightning suppression, the few times I have used they it has made a bad problem just disappear.
get the right type (data rs422/485) its a low voltage type.
If this is that big of a problem I would just put them, at least at the worse panels.
and if it is not lightning it still may fix the problem.
Re: some problem regarding est-3 network card rs485
it happens when there is power interruption on the area...i will check the spec's of that lightning suppression..thanks