Re: Sprinkler Pre-Action System
Posted: Sat Oct 06, 2012 7:33 am
Your sprinkler company is responsible for testing and maintaining . Tha alarm co. is responsible for there connection to pre-action panel. I prefer for sprinkler co to discharge there own panel , but that dose not always happen. Yes you can have relay from fire panel . It should be dumped by 2 devices , one being a field device and low air pressure .Some times 2 field devices, There are other options to to activate this as well. This should be connected to some communicator , most times by module that reports to the building fire panel.