is smoke detector required inside the wash room?
Posted: Sat Jun 28, 2014 5:53 am
by peermoh80
is smoke detector required inside the wash room? as per NFAP 72.
Re: is smoke detector required inside the wash room?
Posted: Sat Jun 28, 2014 4:03 pm
the question is not does NFPA require a smoke in the rest room
is it required by your local code which is not a simple question.
NFPA tells you how to do it not what do to.
to try and help you tell us about your situation.
ie. Is this an inspection, new install, type of building, sprinklered, type of occupancy, who is asking for it and where is this.
Posted: Tue Jul 01, 2014 1:36 am
by peermoh80
Mr.Leo,
this is commented by third party inspector in a shopping mall project.
ofcourse this is an installation inspection
Area: Public Toilet and wash rooms.
Posted: Thu Jul 03, 2014 8:40 pm
by old_tech
You need to refer to the guidelines published by the AHJ. In some areas buildings that are fully sprinkled, only electric, it, elevator and mechanical rooms reguire detectors. Some also require smoke or heat detectors in pantry's.
Posted: Sun Jul 06, 2014 2:20 am
by peermoh80
But NFPA state that to consider nuisance alarm due to steam,moisture and dust.
from my point of view toilets and wash rooms are moisture content area.hence its better to avoid the smoke detector in such areas.
Posted: Wed Jan 24, 2018 10:40 am
by akrajib143
I want to know if the building fully covered by the automatic sprinkler (Fire Protection), any Fire Alarm System Devices is required or not as per NFPA Guideline.
the Floor is fully covered by the central air-condition system, the which Detector we should be consider for Fire Alarm System Design.
Thanking you,
Enamul
Posted: Wed Jan 24, 2018 9:40 pm
generally smokes are not put in wash rooms, usually it is heats
I assume a wash room is a bathroom/restrooms
I had a job the fire marshal wanted smokes in the restrooms, so you just do it
if it is total coverage, every room is every room