Burglar alarm panels used as commercial fire alarm panel

Post Reply
garricker
Posts: 2
Joined: Thu Nov 06, 2014 11:07 pm

Burglar alarm panels used as commercial fire alarm panel

Post by garricker »

Hi all,

is it allowable per NFPA 72 to you use a burglar panel such as DSC powerseries, GE Networx, Honeywell Vista etc etc as commercial FACP or a combination of burglar and fire?

if not where in NFPA72 does is say that?

since we have problem bidding on projects since our competitors our using those type of panel for FACP or combination of burglar and fire for commercial use..

please advice
pyrosucks
Posts: 106
Joined: Wed Feb 23, 2011 9:08 am

Re: Burglar alarm panels used as commercial fire alarm panel

Post by pyrosucks »

Unfortunately, it is allowed, but only if the equipment is UL listed for commercial fire use. Not all models are listed for this purpose, and many that are require special add on modules and power supplies to meet this requirement. Easy way to tell, if it has a plug in transformer, not listed.


Example
Ademco vista 32 - not listed
Ademco vista 32FB - listed, but must use special power supply, add a card for two phone lines, must use the "fire style" keypad, etc