EST2 - DL1 & DL2 Dialer tips
Posted: Thu Oct 22, 2009 1:20 pm
Introduction:
From time to time it may be necessary to make programming changes to the dialer, examples include new CMS (Central Monitoring Station) numbers or simply adding a 9 to an existing number in order to dial out an outside line. Listed below are some programming tips that may help you re-enter the dialer programming mode and make the necessary changes: (These tips are for both the DL-1 and DL-2)
1. Enter the program mode password (4727) between 3 and 8 seconds after panel powerup. Timing is critical and it may require more than one attempt.
2. With a touch tone phone connected to the dialer enter the password, then press the dialer enable/ disable switch, leave the programming phone off the hook. In 15-20 minutes the dialer’s green LED should light steady indicating that the password has been accepted.
3. Disconnect both primary and secondary phone lines. Note: You will have 0026 and 0027 faults on the 2-LCD from having both lines disconnected (EST2(N) Only). The dialer will be attempting to dial out and will fail its attempts in 25-30 minutes. When the message “dial out attempt has failed” appear enter the password. (For the DL-1, slow single flashing amber indicates module/phone trouble, wait 25-30 minutes before entering password).
Note: You need only to enter the programming step(s) in which you wish to edit if the dialer was initially programmed.
To Verify Programming Information:
1. Press the “*” key and enter the respective programming item number into the dialer using the programming phone.
2. Press the “#” key. The phone will sound out the programming item’s contents. 3. Repeat Steps 1 & 2 until all changes have been verified.
Dialer codes
Event Code
Fire alarm report codes 01-32
Fire alarm restore codes 41-72
Normal 24 hr check-in 90
Abnormal 24 hr check-in 91
Supervisory alarm 92
Trouble 93
Trbl/Supv Restore-94
AC power fail 96
Battery trouble 97
Telephone line trouble 98
Dialer disabled 99
From time to time it may be necessary to make programming changes to the dialer, examples include new CMS (Central Monitoring Station) numbers or simply adding a 9 to an existing number in order to dial out an outside line. Listed below are some programming tips that may help you re-enter the dialer programming mode and make the necessary changes: (These tips are for both the DL-1 and DL-2)
1. Enter the program mode password (4727) between 3 and 8 seconds after panel powerup. Timing is critical and it may require more than one attempt.
2. With a touch tone phone connected to the dialer enter the password, then press the dialer enable/ disable switch, leave the programming phone off the hook. In 15-20 minutes the dialer’s green LED should light steady indicating that the password has been accepted.
3. Disconnect both primary and secondary phone lines. Note: You will have 0026 and 0027 faults on the 2-LCD from having both lines disconnected (EST2(N) Only). The dialer will be attempting to dial out and will fail its attempts in 25-30 minutes. When the message “dial out attempt has failed” appear enter the password. (For the DL-1, slow single flashing amber indicates module/phone trouble, wait 25-30 minutes before entering password).
Note: You need only to enter the programming step(s) in which you wish to edit if the dialer was initially programmed.
To Verify Programming Information:
1. Press the “*” key and enter the respective programming item number into the dialer using the programming phone.
2. Press the “#” key. The phone will sound out the programming item’s contents. 3. Repeat Steps 1 & 2 until all changes have been verified.
Dialer codes
Event Code
Fire alarm report codes 01-32
Fire alarm restore codes 41-72
Normal 24 hr check-in 90
Abnormal 24 hr check-in 91
Supervisory alarm 92
Trouble 93
Trbl/Supv Restore-94
AC power fail 96
Battery trouble 97
Telephone line trouble 98
Dialer disabled 99