Page 1 of 1
DL2
Posted: Thu Jun 06, 2019 4:44 pm
by vectrasoundz
Hey guys i did a search but didnt come up with anything, installed a DL2 on a panel that never had one, how do i get the panel to dial on events?
Re: DL2
Posted: Fri Jun 07, 2019 6:57 pm
by Leo
Re: DL2
Posted: Tue Jun 11, 2019 8:55 am
by Leo
Also you need to program the EST2 via the SDU software
Re: DL2
Posted: Tue Jun 11, 2019 10:09 am
by vectrasoundz
ahhhh that is the part there, the smokes and pull have to be put in a dialer group?
Re: DL2
Posted: Sat Jun 15, 2019 12:40 pm
by Leo
the DL2 is a 4-2 format which I hope is not a problem
You will need to program the EST2 panel
you could put an I/O panel in.
the EST2 is old
the I/O will give you CID format
Re: DL2
Posted: Sat Jun 15, 2019 12:43 pm
by vectrasoundz
we wanted to change it to an IO but they didn't want to spend the money. Thought it did CID, that is a problem.......
Re: DL2
Posted: Sat Jun 15, 2019 1:04 pm
by Leo
money money money, nobody wants to send it.
the I/O does CID
EST2 is only 4-2, if you can program it, it will work.
4-2 will work on the starlink or telguard (do not use the telguard TG7)
one general supv and a few different troubles from the EST2
but 32 different fire alarm zones/groups