2-dact

Posted: Sat May 20, 2017 4:04 pm
by Birdem
Hello, I have a troubleshooting question regarding the est-2 2-dacts. I was sent on a service call there was zone 94 and zone 92 reporting to central station. zone 94= smoke and zone 92= low air pressure switch. I checked the panel was normal, I found a ground on a pullstation which had nothing to do to those zones and fixed that issue. I had central station reset the zones and the zones came back again with a normal panel. Im leaning towards there maybe be a programming issue with the 2-dact, I checked the panel db date and it showed it was downloaded not to long ago. Anyone would know what would be the next step?

Re: 2-dact

Posted: Sun May 21, 2017 2:53 pm
by old_tech
See here for the generic codes you are transmitting in 4+2 format, not contact ID
http://www.thealarmtech.com/manuals/EST ... amming.pdf

Re: 2-dact

Posted: Tue May 23, 2017 8:32 am
by Birdem
Thank you