Table 4-2: System fault messages
Message Description
0004 / Open fault, 2-PPS(/6A) Brownout or loss of ac power caused by an:
• Input voltage below 85% of rating
• Open on the ac input fuse (F1)
0005 / Ground Fault, System Ground
• Pinched wire between device and electrical box
• Nicked wire insulation
0006 / Internal Fault Abnormal internal voltage due to a 2-PPS(/6A) failure.
0007 / Communications Fault, Local Controller (See Table 4-12 for LED indications on the 2-MCM.) Main Controller Module (2-MCM) not communicating with the 2-PPS(/6A), caused by a:
• Loose or defective ribbon cable*
• Defective 2-MCM * Check J1 on the 2-MCM and the 2-PPS(/6A).
0008 / Communications Fault,
Expansion Controller (See Table
4-13 for LED indications on the 2-
LCX.)
Expander Loop Module (2-LCX) not communicating with
the 2-PPS(/6A), caused by a:
• Loose or defective ribbon cable*
• Defective 2-LCX
*Check J1 on the 2-LCX and the 2-MCM.
0009 / Internal Fault, Watch-dog
Time-out
Watch-dog timer restart failure: 2-MCM failure
0010 / Internal Fault, LCD Display
Table 4-15
Communication failure between the 2-LCD and the
2-MCM, caused by a:
• Loose or defective ribbon cable*
• Defective 2-LCD
*Check J1 on the 2-LCD and J2 on the 2-MCM.
0011 / Internal Fault, Local
Annunciator
Front panel annunciator module not communicating with the 2-MCM
0012 / Internal Fault, Dialer Fault on dialer module or associated wiring caused by:
• Improper programming of the dialer
• Telephone line problems
0013 / Internal fault, printer or
external command port (ECP)
Problem on RS-232 port or device caused by:
• Off-line status of the printer or ECP
• Incorrect device wiring (Pins 2 and 3 on the printer
cable)
0014 / Communication fault,
2-PPS(/6A)
Communication failure between the 2-MCM and the
2-PPS(/6A), caused by a:
• Loose or defective ribbon cable*
• Defective 2-PPS(/6A)
*Check J1 on the 2-PPS(/6A) and the 2-MCM.
0015 / Class A fault, Loop 1 Wiring Open or short on one path of the 2-MCM Signature data
circuit (SDC)
0016 / Internal Fault, Loop 1
Device Mapping Error
The 2-MCM SDC is in the process of mapping the circuit. This fault should clear itself when mapping is complete. Mapping may take up to 30 minutes per circuit.
0017 / Internal Fault, L1 Dev.
Personality
A personality code mismatch exists on the 2-MCM SDC.
0018 / Internal Fault, Loop 1
autoconfigure
The 2-MCM SDC could not properly configure the circuit.
0019 / Internal Fault, Loop 1 Int.
Memory
A memory mismatch exists between the actual data from the SDC and the expected data in the 2-MCM.
0020 / Class A fault, Expansion
Loop
Open or short on one path of the 2-LCX SDC.
0021 / Internal Fault, Loop 2
Device Mapping Error
The 2-LCX SDC is in the process of mapping the circuit. This fault should clear itself when mapping is complete. Mapping may take up to 30 minutes per circuit.
0022 / Internal Fault, L2 Dev.
Personality
A personality code mismatch exists on the 2-LCX SDC.
0023 / Internal Fault, Loop 2
autoconfigure
The 2-LCX SDC could not properly configure the circuit.
0024 / Internal Fault, Loop 2 Int. Memory
A memory mismatch exists between the actual data from the SDC and the expected data in the 2-LCX.
0025 / Dialer Internal Memory
Fault (See Table 4-17.)
An internal error has occurred. Turn the power off and on again. Replace the DL2 if the fault remains.
0026 / Dialer Phone Line 1 fault An electrical fault on telephone line 1 caused by:
• A bad connection between J1 and the telephone jack
• An inoperative telephone line
Note: The fault may take up to two minutes to clear after the repair.
0027 / Dialer Phone Line 2 fault An electrical fault on telephone line 2 caused by:
• A bad connection between J2 and the telephone jack
• An inoperative telephone line
• A configuration error*
*If the DL2 is configured for 1-line operation, this error means J2 is connected to a good phone line. Disconnect the line to clear the error. The fault may take up to two minutes to clear after the repair.
0028 / Call-out Not Completed By Dialer
• The dialer reached the maximum number of call attempts.
• The telephone company has technical problems.
• The receiver is down.
0029 / Dialer manually disabled The dialer disconnect switch was pressed or:
• The dialer is new and needs programming
• The dialer is in the programming mode
See the DL2 installation sheet for programming instructions on the DL2.
0030 / Test Mode Active Someone initiated a test by pressing the 2-LCD Test
switch. The message will go away when the test ends. See
the System Operation Manual for more information.
0101 to 0196 - Device/line Fault or Device communications fault
Trouble on Signature detector wired to the 2-MCM having an address from 0101 to 0196
0201 and 0202 - Open fault (See Table 4-14.)
An open on the 2-MCM NAC caused by:
• An incorrect or missing EOL resistor
• A miswired circuit or intermittent connections
• A broken conductor
0201 and 0202 - Short fault 2-MCM NAC shorted because of a:
• Polarized device reversed on the circuit
• Defective notification appliance
• Miswired circuit
0203 to 0296, Device/line Fault or
Device communications fault
Trouble on a Signature module wired to the 2-MCM having an address from 0203 to 0296
0301 to 0396 - Device/line Fault or
Device communications fault
Trouble on Signature detector wired to the 2-LCX having an address from 0301 to 0396
0401 and 0402 - Open fault An open on the 2-LCX NAC caused by:
• An incorrect or missing EOL resistor
• A miswired circuit or intermittent connections
• A broken conductor
0401 and 0402 - Short fault 2-LCX NAC shorted because of a:
• Polarized device reversed on the circuit
• Defective notification appliance
• Miswired circuit
0403 to 0496 - Device/line fault or
Device communications fault
Trouble on Signature module wired to the 2-LCX having an address from 0403 to 0496
XX97* Comm Fault Primary Comm Channel (xx = 10-40 or 44-63)
XX98* Comm Fault Secondary Comm Channel (xx = 10-40 or 44-63)
XX99* Internal Fault Card/Supervision (xx = 10-40 or 44-63)
41XX 2-AAC Audio Controller
faults
EST2 - System fault messages
-
- Posts: 1
- Joined: Wed May 12, 2021 10:32 am
Re: EST2 - System fault messages
Has anyone had issues with only “j2”
Phone lines are good, j1 is good, j3 is making connection.. but j2 fails the 24 hour check In every day