watchdog fault 0009 and 0016 fault

Post Reply
Sam
Posts: 29
Joined: Sun Oct 17, 2010 6:38 pm

Re: watchdog fault 0009 and 0016 fault

Post by Sam »

Mapping fault on loop 1 for 0016.
ny_offered
Posts: 16
Joined: Mon Nov 01, 2010 10:29 pm

Re: watchdog fault 0009 and 0016 fault

Post by ny_offered »

0016 is internal fault isn't it?
Sam
Posts: 29
Joined: Sun Oct 17, 2010 6:38 pm

Re: watchdog fault 0009 and 0016 fault

Post by Sam »

No, 0016 is mapping fault on loop 01.
Trouble 0009 is a 2-MCM failure.
ny_offered
Posts: 16
Joined: Mon Nov 01, 2010 10:29 pm

Re: watchdog fault 0009 and 0016 fault

Post by ny_offered »

THIS IS HAPPEN AFTER ELECTRICIAN ADD 3 NEW MODULE(CR, CT-2). SO I BYPASSED NEW MODULES BUT SAME. THAN I TRIED AFTER DISCONNECT LOOP1 BECAUSE 0016 IS LOOP 1 FAULT.
BUT STILL JUST DISPLAY WATCH-DOG 0009.
ny_offered
Posts: 16
Joined: Mon Nov 01, 2010 10:29 pm

Re: watchdog fault 0009 and 0016 fault

Post by ny_offered »

fixed problem. loop 1 wire was connected to new devices reverse. reprogram done.
ny_offered
Posts: 16
Joined: Mon Nov 01, 2010 10:29 pm

watchdog fault 0009 and 0016 fault

Post by ny_offered »

EST2 had OO16 FAULT. THAN CHANGE TO WATCHDOG 0009 AND KEEP RESTART. SO I POWER DOWN AND UP, BACK TO 0016.
ANY IDEA? BAD 2-mcm?