Siemens FC924 Panel with 2 FT2014 Annunciators

Post Reply
dougncin
Posts: 31
Joined: Tue Jan 09, 2018 9:14 pm

Re: Siemens FC924 Panel with 2 FT2014 Annunciators

Post by dougncin »

Here you go. Yes you can disable ground fault but don't recommend it
Attachments
351796581-A6V10333434-FS20-Commissioning-Maintenance-Troubleshooting-Manual.pdf
(6.28 MiB) Downloaded 1333 times
Mfssystems
Posts: 11
Joined: Sat Feb 10, 2018 11:22 pm

Re: Siemens FC924 Panel with 2 FT2014 Annunciators

Post by Mfssystems »

Thanks for manual
I saw that S33 has dip switch to disable ground fault detection Except on the rs485 circuit..
Is there a way to disable ground fault on the rs485 circuit?
And also, what is degrade mode?
I see the term in manual. And also, my ground fault on panel says “ground fault (-) degrade interface”
Does this degrade interface mean ground fault on a specific thing?
dougncin
Posts: 31
Joined: Tue Jan 09, 2018 9:14 pm

Re: Siemens FC924 Panel with 2 FT2014 Annunciators

Post by dougncin »

check S38 and S39
Mfssystems
Posts: 11
Joined: Sat Feb 10, 2018 11:22 pm

Re: Siemens FC924 Panel with 2 FT2014 Annunciators

Post by Mfssystems »

Got it... S38 and S39, Jumper OFF

thx
Mfssystems
Posts: 11
Joined: Sat Feb 10, 2018 11:22 pm

Siemens FC924 Panel with 2 FT2014 Annunciators

Post by Mfssystems »

I have a Siemens FC924 Panel with 2 FT2014 Annunciators
Issue is what appears to be a swinging ground Fault

Trouble that pops up a few times a day is " Ground fault (-) Degrade Interface"
I thought one of the two Annunciators was bad causing this problem.
Annunciator was packed with drywall dust and you could not see what was on the screen.
But after replacing ANN, problem still persists..
I am leaning towards Swinging Ground fault on wiring..
Anyone know what "Degrade Interface" on FC924 Panel is?
Is there a way to disable Ground fault monitoring on this panel for testing purposes?
Anyway have a Manual on this Siemens FC924?
Post Reply