Edwards Signaling" vs "Kidde Edwards" vs "EST IO"
The EST and Kidde are very similar
All three use different software
I/O panel DIFFERENT VERSIONS
EST - IO-CU
KIDDE - VS-CU
Edwards Signaling FX-CU FSA-CU
Software you should have on your computer
Panel Version 1.2 will need CU 3.5
FSA-CU 3.5
FX-CU 3.5
FX-CU 4.11
IO-CU 4.11
IO-CU 3.5
VS-CU 4.11
VS-CU 3.5
**************
EST IO - IO-CU 4.11
EST DEALER
IO-CU 4.11
C:\Program Files\Edwards Software\IO-CU\" IO-4.11
IO64
IO500
IO1000
**************
Kidde DEALER
VS-CU 4.11
VS1 2 4
"C:\Program Files\Kidde\VS-CU\"
**************
Kidde Edwards "GE FireworX UTC"
Edwards Signaling - FX-CU V4.11
FX-CU - ADI Can buy
C:\Program Files\Kidde\FX-CU\" FX-CU 4.11
DOWNLOAD FROM http://kiddefx.kidde.com/Home/Software
FX-64
FX-254
FX-1000
**************
OLDER PANEL - FSA250 REPLACED WITH FX-1000
Edwards Signaling - FSA-CU 3.5 KIDDE
C:\Program Files\GE\FSA-CU\" FSA-CU 3.5
DOWNLOAD FROM https://edwards-signals.com/index.cfm?p ... l=25&sid=0
FSA64
FSA250
Conventional
FSC302
FSC502
FSC1004
FS1004
FS502
FS302
Kidde - Edwards
http://kiddefx.kidde.com/Home/Index
Edwards Signaling
https://www.edwards-signals.com/
software - FSA-CU 3.5
https://www.edwards-signals.com/index.c ... l=25&sid=0
"Edwards Signaling" vs "Kidde Edwards" vs "EST IO"
Re: "Edwards Signaling" vs "Kidde Edwards" vs "EST IO"
Hello
I have installed and programmed the 3 panel lines.
The vigilant series of edwards is now vigilant kidde. With the vigilant vs1 and vs2 I had many problems: when there are troubles and it is unattended the keyboard breaks down and the situation is irreversible. I had up to 8 clients in that situation. In buildings where they were attended and recognized any trouble in fast form, it has worked impeccably.
The Kidde watch series is the same, only the label has been changed, the series of 2 loops is no longer manufactured and in its replacement is the 4-loop VS4 series. So far I do not have the problem of the previous series, but it must be because it has only recently installed.
The programming is friendly, but also presents the same problems of random decalibration of smoke detectors as SIGA-PS and is irreversible so clean it.
The IO panel of this has not given me the aforementioned problems. The detectors if they present the same problem, so the classic problem of mapping.
But in summary: functionally both series are the same.
I have installed and programmed the 3 panel lines.
The vigilant series of edwards is now vigilant kidde. With the vigilant vs1 and vs2 I had many problems: when there are troubles and it is unattended the keyboard breaks down and the situation is irreversible. I had up to 8 clients in that situation. In buildings where they were attended and recognized any trouble in fast form, it has worked impeccably.
The Kidde watch series is the same, only the label has been changed, the series of 2 loops is no longer manufactured and in its replacement is the 4-loop VS4 series. So far I do not have the problem of the previous series, but it must be because it has only recently installed.
The programming is friendly, but also presents the same problems of random decalibration of smoke detectors as SIGA-PS and is irreversible so clean it.
The IO panel of this has not given me the aforementioned problems. The detectors if they present the same problem, so the classic problem of mapping.
But in summary: functionally both series are the same.
Re: "Edwards Signaling" vs "Kidde Edwards" vs "EST IO"
what is the device compatibility between panels.
Re: "Edwards Signaling" vs "Kidde Edwards" vs "EST IO"
Hello my friends, I have worked in Chile with several types of alarm, recently I have been asked for an alarm that did not stop ringing, when I checked the panel, it is a Vigilant VS2, which shows a trouble message on the screen (I can't remember exactly what it is) but the truth is that it turns on the problem led. In addition to this, the panel does not respond to any touch, none of the buttons work. Do you have any idea what I can do in this case?
isatronix wrote:Hello
I have installed and programmed the 3 panel lines.
The vigilant series of edwards is now vigilant kidde. With the vigilant vs1 and vs2 I had many problems: when there are troubles and it is unattended the keyboard breaks down and the situation is irreversible. I had up to 8 clients in that situation. In buildings where they were attended and recognized any trouble in fast form, it has worked impeccably.
The Kidde watch series is the same, only the label has been changed, the series of 2 loops is no longer manufactured and in its replacement is the 4-loop VS4 series. So far I do not have the problem of the previous series, but it must be because it has only recently installed.
The programming is friendly, but also presents the same problems of random decalibration of smoke detectors as SIGA-PS and is irreversible so clean it.
The IO panel of this has not given me the aforementioned problems. The detectors if they present the same problem, so the classic problem of mapping.
But in summary: functionally both series are the same.