On a CAB5, a CPU-3 and PPS was downloaded and configured ok, then while downloading the added SDDC1 card CPU Fail and SUP LEDs came on with a steady buzzer.
Changed the CPU, this time while downloading to the new CPU, after almost 8% was done CPU Fail and SUP LEDs came on with regular buzzer and time out happened for a few attempt. You can hear the pulsating sound (like when there is a short circuit) seems like a onboard relay acting.
Re: EST3 Downloading Issue
Posted: Sat Oct 20, 2012 6:03 am
by Leo
are you downloading direct or over the network?
Re: EST3 Downloading Issue
Posted: Sat Oct 20, 2012 11:03 am
by ALIT
It’s a single panel for now.
I tried both single step and network at 19.2 and slower and faster baud rate too.
Re: EST3 Downloading Issue
Posted: Sun Oct 21, 2012 7:48 am
by pooriyasms
Try to use another version of SDU
Re: EST3 Downloading Issue
Posted: Sun Oct 21, 2012 9:32 am
by ALIT
I did, tried with Vesion 3.5,3.71, 4.0
Re: EST3 Downloading Issue
Posted: Thu Feb 14, 2013 3:56 pm
by hijazih
it seems u downloaded on the sddc1 using a single step and connecting to the cpu. no solution for this except replacing the cpu.
Re: EST3 Downloading Issue
Posted: Thu Feb 14, 2013 6:53 pm
by ALIT
I had the panel examined by EST3 certified engineer and the found the power supply faulty.
Problem solved.
Re: EST3 Downloading Issue
Posted: Sun Feb 17, 2013 8:21 pm
by Leo
yeah that was the next thing I thought it was.
the power supply yeah
Re: EST3 Downloading Issue
Posted: Sun Feb 17, 2013 10:57 pm
by ALIT
That’s right, right in the beginning I explained that at what point trouble starts and that I changed the CPU …