Device programming

Posted: Tue Sep 18, 2012 12:51 am
by Amber
Hiii,

I need one information that, if I replaced some devices against the existing faulty devices then there is any possibility to accept that devices (As same level text) to EST-3 panel without SDU programming. or It must be needed to prgramming with SDU software and download to Panel.


Thanks
Amber

Re: Device programming

Posted: Sun Sep 30, 2012 3:44 am
by pooriyasms
Dear friend

As I know any change with text of devices needs SDU programming.
So you would not be able to change the text of a device without using SDU programming.

Re: Device programming

Posted: Mon Oct 01, 2012 7:10 pm
by Leo
you can change devices on the SLC loop as long as they are the SAME type of device and the device you are changing is not on the SLC loop as a Balanced Device.

what is a Balanced Device check other posts, it is a long story

Re: Device programming

Posted: Thu Oct 11, 2012 11:21 pm
by Amber
I want to change one SIGA-CT1 against the installed faulty CT1 in a same position, so shall i need SDU programming against it or any process having to do this??

Can u explain me about the SLC loop?

Re: Device programming

Posted: Mon Oct 15, 2012 3:40 pm
by Leo
there is a small chance you will need the SDU to reload the panel/SLC loop after changing a devices on a siga SLC line.
if the device is a balanced device you will need the SDU - http://www.thealarmtech.com/forum/viewt ... nced#p1686
Most cases you will be fine just changing out the devices.

you could write a small book on how the Siga SLC loop works, most techs that work on it would start with the word "shitty".