Hi Leo,

I have issues with "All Call" Button as well as with zone paging, when evac channel is working there is no problem, but the moment page channel is activated, after a few seconds our remote amplifiers (SIGA-AA50) go into trouble on output 1. Do you know what could be wrong with the rules or configuration?. We are using 3-ASU, 3-ZA20B, two SIGA-AA50 and ten SIGA-CC1, to provide audio to the speakers.

Thanks in advance.
Marco

Re: All Call

Posted: Tue Jul 17, 2012 4:32 am
by junjun
-your remote amplifier are not receiving signal coming from your zone amplifier.
-check which type of signal your going to feed to your remote amplifier input (1V or 25v).

Re: All Call

Posted: Sat Sep 15, 2012 4:02 pm
by tukalo
set you jumper setting to 1v or 25v/70v located on the left side facing the aa50 on the input terminal. your wire connection and jumper setting must be on the same setting or terminal.