Map Fault
Posted: Mon Jun 25, 2012 3:46 pm
by ahmed_nas
sometimes when i read a SIGA loop the it starts to map and falls down a lot of times, and in the end it settles as a map fault.
I tried to swap the IN with The OUT loop cables but the problem persists.
What can i do i cant fix the problem.
Thanks
Re: Map Fault
Posted: Fri Jul 13, 2012 2:50 pm
by tukalo
Check thoroughly each of your device installation or your base. One of your device is faulty. First check your isolator bases, the connection of in and out negative. Then your sounder bases if you have in the loop, if not then procced to the heat detectors, maybe one of it is in internal trbl. Make sure your loop return for th loop is 15 volts and above. If it will go below the 15 volts, then one of your standard base is the problem.
Re: Map Fault
Posted: Fri Oct 05, 2012 8:29 pm
by Jmcd57
I got a FAULT 1 on a data card , can anyone explain? I have talked to tech support and did not get a good answer.
Re: Map Fault
Posted: Fri Oct 05, 2012 9:36 pm
by Leo
joe call 856.240.0911
Re: Map Fault
Posted: Thu Feb 07, 2013 7:26 pm
by Luber Gene
Can somebody explain exactly how the diagnostics current chain and device response chain works? I just don't get it when troubleshooting map faults.