150 detector get fault alarm

donpccc
Posts: 37
Joined: Mon Dec 13, 2010 9:26 pm
Location: Viet Nam
Contact:

150 detector get fault alarm

Post by donpccc »

Hi every one,
Rthis is bad month for us. We using est-3 control panel, Siga-ct1 + sim-intl for addressible monitor. And using 711u, 721ut, ec heat detector. But now many zone of smoke detector get fault alarm while the room is verry clean and heat detector working normal.
Please help us advice,
300 over 2000 detector get fault alarm.

Thank you,
Don nguyen
juanjose
Posts: 26
Joined: Wed Dec 14, 2011 2:07 pm

Re: 150 detector get fault alarm

Post by juanjose »

R YOUR DETECTORS 4WIRE ONES?

MAYBE YOUR POWER IS NOT WORKING PROPERLY, AND THEY GOES INTO FAULT FOR THAT REASON.

SEEMS THAT YOUR PROBLEM IS YOUR POWER SUPPLIES YOU'D BETTER INSTALL CT1'S TO MONITOR THEM
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: 150 detector get fault alarm

Post by Leo »

The EST SLC loop does have a history of siga smokes detectors false alarming,
I have not found the cause, although I think it is noise on the SLC loop.

To try and get a better idea of the problem.
You have 3000 CT1s connected to 4/2 wire smokes and the CT1's are false alarming?
give he more info: any siga smokes, "IS THE WIRE SHIELDED OR UNSIELDED", are the SLC loops full.

If you find the problem I would like to know what you found.
anthony08
Posts: 11
Joined: Thu Apr 07, 2011 11:57 pm

Re: 150 detector get fault alarm

Post by anthony08 »

i have the same problem, the alarm usually occurs at noon or night time, I observe the sim intl at this time, it goes into alarm then restores to normal in a matter of second, the siga-ct1 goes into alarm. What I did was configure the siga-ct1 to 'general alarm' then set it to 'delayed alarm' .
juanjose
Posts: 26
Joined: Wed Dec 14, 2011 2:07 pm

Re: 150 detector get fault alarm

Post by juanjose »

THE PERSONALITY OF GENALARM, MAKES YOU CONFUSE SINCE ANY ALARM WILL TRIGGER YOUR NAC´S, IS BETTER IF YOU CHANGE THAT PERSONALITY.
shashishashu
Posts: 15
Joined: Fri Dec 14, 2012 5:15 pm

Re: 150 detector get fault alarm

Post by shashishashu »

how many det are connected to a simintl? check the current sink...
briac
Posts: 93
Joined: Sat Jul 28, 2012 10:16 am
Location: GMT+3

Re: 150 detector get fault alarm

Post by briac »

check first your wiring,
check also if there is no perturbation around your CT1 like X ray ;high voltage...
it was a bad day for me one moth ago.
courage!!
serdy
Posts: 3
Joined: Sat May 09, 2009 12:15 am
Location: manado

Re: 150 detector get fault alarm

Post by serdy »

shashishashu wrote:how many det are connected to a simintl? check the current sink...
Last edited by serdy on Tue Jun 18, 2013 5:08 am, edited 1 time in total.
donpccc
Posts: 37
Joined: Mon Dec 13, 2010 9:26 pm
Location: Viet Nam
Contact:

Re: 150 detector get fault alarm

Post by donpccc »

serdy wrote:
shashishashu wrote:how many det are connected to a simintl? check the current sink...
maximum 20 pcs 711u per simntl
- that's is stupid way to fixed error.
The first i call GE-UTC Product manager man from Singapore direct to the Site. After, confirm the devices may be error!
Change 700 detector with new ones. Now the error seem decrease but some time has get fault alarm..
This project..
fcefed
Posts: 1
Joined: Thu Mar 06, 2014 9:47 pm

Re: 150 detector get fault alarm

Post by fcefed »

Had similar problem found 480v for pressure fan going through siga-cr back feeding through relay onto slc loop. Separated high voltage from relay via a Pam relay no problems similar since.