Fire Suppression Systems (SIGA-REL module)
Posted: Tue Nov 10, 2009 5:41 am
by sarian
I am going to equip two server rooms with FM-200 fire suppression systems, the rooms are near each other.
As I read SIGA-REL data sheet, it seems that one SIGA-REL module can extinguish two fire suppression zones, am I right?
would you please let me know what kind of devices I need, my assumption is:
- SIGA-REL 1 Pc
- Manual Release Station 2Pc
- Abort Station 2Pc
- Service Disconnect Switch 2Pc
- End-of-Line Relay 2Pc
Do I need any thing else?
Can I connect two Abort Station or Manual Release Station to one SIGA-REL module for controling two different fire suppression zones?
Thanks,
Reza
Re: Fire Suppression Systems (SIGA-REL module)
Posted: Tue Nov 10, 2009 7:50 pm
by Leo
over here in this parts we ONLY take hits or trips from the suppression systems, we never control it.
it's a whole nother group of people.
I don't thing I am going to be able to help you.
Re: Fire Suppression Systems (SIGA-REL module)
Posted: Thu Nov 12, 2009 8:58 am
by mikbz
sarian wrote:I am going to equip two server rooms with FM-200 fire suppression systems, the rooms are near each other.
As I read SIGA-REL data sheet, it seems that one SIGA-REL module can extinguish two fire suppression zones, am I right?
would you please let me know what kind of devices I need, my assumption is:
- SIGA-REL 1 Pc
- Manual Release Station 2Pc
- Abort Station 2Pc
- Service Disconnect Switch 2Pc
- End-of-Line Relay 2Pc
Do I need any thing else?
Can I connect two Abort Station or Manual Release Station to one SIGA-REL module for controling two different fire suppression zones?
Thanks,
Reza
I have little bit simple FM200 system with SIGA-REL:
-Siga-Rel 1PC
-Yellow Manual Release Station 1Pc
-Horn 1Pc
-and addition MCT2 1PC for FM200 Pressure Switch
Also you should add rule for RESET:
RESET: OFF -HIGH '*_PRE_RELEASE1_*';
for silent horn after reset.
Re: Fire Suppression Systems (SIGA-REL module)
Posted: Mon Nov 16, 2009 9:43 am
by sarian
Thanks Mikbz,
You are right, as per a EST engineer statment, 1 SIGA-REL is used for one zone. It is capable of releasing 2 separate bottles, of gas etc., but they work together. If the rooms need to work independently, then you need 2 SIGA-REL modules.
The required equipments for extinguishing two zones are:
SIGA-REL 2Pcs
278A–REL Manual Release Station- Double Action 2Pcs
RELA-ABT Manual Abort Station 2Pcs
RELA-SRV Service Disconnect Switch 2Pcs
G1R–HDVM Temporal horn-strobe multi-cd - RED 4Pcs
439D - 6AW–R 6” Bell 24Vdc Red 2Pcs
FS.C I don’t know what it is!? 2Pcs
He also provided me a very good SIGA-Technical Manual which is 70 pages, I uploaded it in mu website:
http://www.sarian.ir/images/SIGA-REL_Manual.pdf
This also SIGA-REL general data sheet:
http://www.sarian.ir/images/SIGA-REL.pdf
Best,
Reza