Page 1 of 1

Rail Module Communication Fault

Posted: Wed Jun 24, 2009 3:08 pm
by hijazih
When turning on the EST Panel for the first time one of the troubles being noticed is
" 01070601 Rail Module Communication Fault"
at 0107**** location the component is 3-ASU.
it is being noticed also that the all the LEDs of the ASU in on all the time.

Thanks for any suggested idea..

Re: Rail Module Communication Fault

Posted: Wed Jun 16, 2010 8:55 am
by phongred
i have same problem, i change new CPU, it ok

Re: Rail Module Communication Fault

Posted: Thu Jun 17, 2010 11:13 am
by FireTech
When you see all the Leds flashing or pulsating, that is an indicator that it is in "Comm Fail" Hence... The " 01070601 Rail Module Communication Fault" you are getting..

-- Make sure you have the Cables on correctly between your Chassis. (and seated firmly)

-- Look at your SDU program. What do you have programmed for Rail #2? And, Have you Compiled/Coverted and Loaded your CPU in question?

-- All due respect... You have some troubleshooting to do before you are close to replacing the 3-Cpu.









When turning on the EST Panel for the first time one of the troubles being noticed is
" 01070601 Rail Module Communication Fault"
at 0107**** location the component is 3-ASU.
it is being noticed also that the all the LEDs of the ASU in on all the time.

Thanks for any suggested idea..

Re: Rail Module Communication Fault

Posted: Sat May 17, 2014 11:02 am
by delanil
Panel :est3

Status: Panel shows rail module communication fault after download.
Earlier Panel was working fine
Please suggest a solution.




Thanks for any suggested idea..[/quote]

Re: Rail Module Communication Fault

Posted: Sun May 18, 2014 11:13 pm
by briac
delanil ,
I have the same problem but it desapear like this few seconds or minute after,
I thinks te rail module is busy during the download,
try to reduce the baud at 19200 maximum,
Do not rush the download,do it slowly;
check the RX and TX LED on each module and you will see which one is not responding.

thanks,