EST3 - Reducing Download Time (working on)
Posted: Thu May 14, 2009 9:52 am
Thing to think about: ((( working on))))
1. You can download via the RS232 port of the CPU. You will need a RS232 card at that CPU and you can load from ANY CPU. But are limited to 9600bd.
2. Baud rate 38.4 will not cut the time in half over 19.2, this is because of the wait time between CPU's.
3. If your network is running at 19.2 you can download at 38.4, In most casts you CAN run your network at 38.4
4. The ASU only needs to be loaded if you change the messages
5. The SSDC/SDDC cards only need to be loaded if changes are made to it. ie. add/delete devices. NOT if the labels or descriptions are changed.
6. Try not to change the SDU Version ie. 01.00.00 -> 01.00.01 or you will need to load the SSDC cards.
Check total CPU bits to download,
9600 - 41-45k per minute
19.2 - 52-64k per minutes
38.4 - 93k per minutes - Connected to the rj11 jack and only load that panel
Remember to also upload the device map and check them if its been a while at the site.
3,800k/73 minutes = 53 per minute
1. You can download via the RS232 port of the CPU. You will need a RS232 card at that CPU and you can load from ANY CPU. But are limited to 9600bd.
2. Baud rate 38.4 will not cut the time in half over 19.2, this is because of the wait time between CPU's.
3. If your network is running at 19.2 you can download at 38.4, In most casts you CAN run your network at 38.4
4. The ASU only needs to be loaded if you change the messages
5. The SSDC/SDDC cards only need to be loaded if changes are made to it. ie. add/delete devices. NOT if the labels or descriptions are changed.
6. Try not to change the SDU Version ie. 01.00.00 -> 01.00.01 or you will need to load the SSDC cards.
Check total CPU bits to download,
9600 - 41-45k per minute
19.2 - 52-64k per minutes
38.4 - 93k per minutes - Connected to the rj11 jack and only load that panel
Remember to also upload the device map and check them if its been a while at the site.
3,800k/73 minutes = 53 per minute