Page 1 of 1
Re: Sounder Base
Posted: Mon Oct 17, 2016 6:35 pm
by Leo
one of two things the CR has been activated or you are wired to the N/C connect.
Re: Sounder Base
Posted: Sun Oct 23, 2016 11:31 am
by riztgh
Thanks Leo,
Can you help me with Rules so that sounder base only activates when the particular detector in alarm.
Re: Sounder Base
Posted: Thu Oct 27, 2016 9:46 am
by Old fire alarm guy
Here's some rules from a job I did in NYC for the combo CO & smoke detectors:
[SMOKE ALARM LOOP 3A 3-5]
ALARM SMOKE 'COSMK_LOOP_3A_*_<N:1-83>' : ON 'TCDR_CH1_LOOP_3A',
ON 'COSMK_LOOP_3A_*_<N>';
[SMOKE ADA ALARM LOOP 3A RM402]
ALARM SMOKE 'COSMK_LOOP_3A_<N:26>_*' : ON -LOW 'STRB_L8_RM402';
[SMOKE ADA ALARM LOOP 3A RM404]
ALARM SMOKE 'COSMK_LOOP_3A_<N:27,28>_*' : ON -LOW 'STRB_L8_RM404';
[SMOKE ADA ALARM LOOP 3A RM502]
ALARM SMOKE 'COSMK_LOOP_3A_<N:59>_*' : ON -LOW 'STRB_L9_RM502';
[CO SOUNDER LOOP 3A 3-5]
COSUPERVISORY 'COSMK_LOOP_3A_*_<N:1-83>' : ON 'TCDR_CH2_LOOP_3A',
ON 'CO_TO_CO',
ON 'COSMK_LOOP_3A_*_<N>';
Sounder Base
Posted: Sat Oct 15, 2016 4:07 am
by riztgh
Hi All,
For sounder bases , we use siga-CR wiring with all sounder base in a floor and ends with 47kohm EOL just like the wiring diagram given in AB4G datasheet. But, when we switch on the power switch, the all sounder bases starts ringing without any alarm. The sounder base will sounds when the smoke detectors experience smoke. Can anyone please help me with rules...