Page 1 of 1

Ground Fault

Posted: Thu May 29, 2014 7:15 pm
by JR75
Just recently upgraded from the IRC-3 to the EST-3 and Fireworks system so still trying to find my way around it. One of the buildings has 2 ground faults. I have these in the past and they have been hard to find. But, on the Fireworks I looked at the Alarm Points and its giving me these codes for the ground faults.


01-01(01-007-01000602)

01-04(01-007-01020677)

Can anyone tell me what these codes are for? I suspect the last set of numbers are the panel/card/port but I was hoping that the rest of it would give me some direction on where to look instead of simply digging for days upon days.

Thanks for any help.

Re: Ground Fault

Posted: Fri May 30, 2014 11:47 am
by Sam
01000602 Power Supply
01020677 first module after power supply.

Re: Ground Fault

Posted: Sun Jun 01, 2014 8:15 pm
by JR75
Sam wrote:01000602 Power Supply
01020677 first module after power supply.
Sam,

Thanks for the reply. I suspected this, but wasn't sure with the 01-01 in front of them. Any hints as to what could possibly be causing a ground fault for both of these, power supply and module?

Re: Ground Fault

Posted: Sun Jun 01, 2014 8:50 pm
by Sam
01-01 is add by FireWorks.
For power supply or cpu if you remove RS232 for Fireworks, ground go off for 01000602.
01020677 which module ?