EST3-pseudo point 0600 - Annunciator Supervision

Post Reply
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

EST3-pseudo point 0600 - Annunciator Supervision

Post by Leo »

EST3-pseudo point 0600 - Annunciator Supervision

pseudo point 0600 indicates a problem with LED or switch module, check the ribbon between the switch module on board.

IE: Point 01000600 - panel 1, slot 0, pseudo 600
- This would be a problem with the main display to panel 1's CPU.

IE: Point 01020600 - panel 1, slot 2, pseudo 600
- This is the annunciator supervision of a LED or switch module that is mounted on the PPS/M module. if the Power supply was replace just check to make sure the annunciator ribbon cable was re-connected properly.

The problem I had was after replacing the PPS/M module I connected the switch ribbon back on to the PPS/M module, but it was not connected before I replaced it. So the Pseudo point 01020600 came in.

search: EST3-pseudo point 0600 - Annunciator Supervision
cmadradi
Posts: 22
Joined: Tue Feb 11, 2014 12:51 am

Re: EST3-pseudo point 0600 - Annunciator Supervision

Post by cmadradi »

Hello Leo,

I have 4 Annunciator 6x3LED, the rules point them to initiate paging or audio channel in each zone. When I press any switch of any annunciator the error you describe appears. When we activate some of the switches in the annunciator, the monitor windows shows that we are oppening the audio channel to the pager, but the led remains off.

Any Advice?
Post Reply