I'm getting 001 LCL Trouble CommunicationFault on RLCD-c
details: P:00 C:** D:0009 Communication fault
RLCD firmware: V02.03.00
Tried eliminating wire dip switch address and boud rate and i'm stuck.
Io 500 panel cat/rev: 13
What can b the problem? Firmware? where can i get updated firmware for i0500 ?
GD
Io500 /annunciator connection issues
Re: Io500 /annunciator connection issues
Firmware should not matter. Did you enable the annunciator in the IO-500 programming? Is there a trouble on the IO-500?
If you only have a trouble at the RLCD, it is not enabled at the main panel.
If you have a comm fault at both locations, its either wiring or setting the correct address on the dip switches.
If you only have a trouble at the RLCD, it is not enabled at the main panel.
If you have a comm fault at both locations, its either wiring or setting the correct address on the dip switches.
-
- Posts: 3
- Joined: Sun Jan 12, 2014 8:44 pm
Re: Io500 /annunciator connection issues
THanks i tried enabling it in panel but gives me alarm, tested the wire and tried assigning different address . does the panel gives address that have to be mach on annunciator ?
i'll try to see if there is address issue or does controlls have to have the key switch but that should not prevent it from working.
GD
i'll try to see if there is address issue or does controlls have to have the key switch but that should not prevent it from working.
GD