3030 with NCA Smoke Control Programming

Post Reply
AustinTylerDean
Posts: 1
Joined: Mon Sep 14, 2020 1:30 pm
Location: Santa Clara, CA

3030 with NCA Smoke Control Programming

Post by AustinTylerDean »

Hello All,

First post here. I program smoke control buildings in the Bay Area. We are in a pickle. IFC 2015 909.16.3 states that "The last control action as indicated by each fire fighter's control panel switch position shall prevail. Control actions shall not require the smoke control system to assume more than one configuration at any one time.".

To us, this seems like the Smoke Control Panel needs to actuate only the last used knob, releasing the previous smoke zone activation despite the position of the knob. I.e. Floor 1 manual control zone turns to ON, then Floor 2 manual control zone turns to ON, the system should release Floor 1 and activate Floor 2.

How in the world would you be able to create a "Last In" logical argument? I.e. Z1 activates with knob turn for Floor 1. Then Floor 2 knob activates, which needs to deactivate Floor 1. If Floor 3 then is turned, Floors 1 and 2 need to deactivate, etc. For 22 floors! This process needs to happen despite the knob positions of the previously activated floors.

Or are we reading these requirements incorrectly? The author of the Smoke Control Report is taking this all verbatim, so I may not have the original intent understood in the code.

Any ideas or help would be greatly appreciated.

Sincerely,
Austin Dean
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: 3030 with NCA Smoke Control Programming

Post by Leo »

did you try calling notifier tech support

maybe a PLC?
Post Reply