Drill Button- Notifier 3030

Posted: Mon Dec 30, 2013 8:46 am
by maverick
In one of the site , after pressing the drill button from Panel ,Some of the floors hooter are getting activate but not for all the floors. As per the requirement all Floors hooter should activate in case of Drill.

Could you please provide the reason & possible cause for this problem?

Also share what we need to check in software database and at panel & Field end to rectify the issue.

Looking forward the reply on ASAP basis.

Thanks

Re: Drill Button- Notifier 3030

Posted: Mon Dec 30, 2013 8:24 pm
by pyrosucks
DRill button does not activate addressable control modules, only on board nacs

Re: Drill Button- Notifier 3030

Posted: Wed Jan 01, 2014 9:02 am
by Leo
I think the nfs-3030 does not have on board nac but the nfs2-3030 (newer version) has one
are all or some of the control modules not turning on?
are the control modules programmed the same
if you trip a alarm and hit alarm silence what happens. do all the H/S stop, do the horns stop and the strobe stay on, does half the building still ring?