Re: what rule have to put to control the elevator with SIGA-

Posted: Mon Jan 07, 2013 9:53 am
by Leo
Let me know if you need more
---------------------------------------------------------------------
{ ---------- ELEVATOR RECALL ----------- }

[RECALL TO MAIN]
ALARM '*2ND*':
ON NSO '*ELEV_MAIN*';


[RECALL TO MAIN 3RD]
ALARM '*3RD*':
ON NSO '*ELEV_MAIN*';

[RECALL TO ALT]
ALARM '*1ST*':
ON NSO '*ELEV_ALT*';

------------------------------------------------------------------------------

{ ---------- ELEVATOR RECALL ----------- }
[ELEV_UNIT1_MACH_1ST]
ALARM '*ELEV_UNIT1_MACH_1ST*':
ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_ALT',
ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_ALT';

[ELEV_UNIT1_SHAFT_2ND] ALARM '*ELEV_UNIT1_SHAFT_2ND*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_MAIN';
[ELEV_UNIT1_LOBBY_1ST] ALARM '*ELEV_UNIT1_LOBBY_1ST*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_ALT';
[ELEV_UNIT1_LOBBY_2ND] ALARM '*ELEV_UNIT1_LOBBY_2ND*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_MAIN';

[ELEV_GLASS_LOBBY_1ST] ALARM '*ELEV_GLASS_LOBBY_1ST*': ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_ALT';
[ELEV_GLASS_LOBBY_2ND] ALARM '*ELEV_GLASS_LOBBY_2ND*': ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_MAIN';

[ELEV_MACY_SHAFT-LOBBY_2ND] ALARM '*ELEV_MACY_*_2ND*': ON NSO 'RELAY_FREIGHT_MACY_RECALL_TO_ELEV_MAIN';
[ELEV_MACY_MACHINE-LOBBY_1ST] ALARM '*ELEV_MACY_*_1ST*': ON NSO 'RELAY_FREIGHT_MACY_RECALL_TO_ELEV_ALT';

[ELE_FOOD SHAFT-LOBBY 2ND] ALARM '*ELEV_FOOD_*_2ND*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_MAIN';
[ELEV_FOOD_LOBBY_1ST] ALARM '*ELEV_FOOD_LOBBY_1ST*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_ALT';
[ELEV_FOOD_machine_1ST] ALARM '*ELEV_FOOD_MACH*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_ALT';

Re: what rule have to put to control the elevator with SIGA-

Posted: Sun Dec 15, 2013 10:03 am
by Nirujan
Is it possible in est3 rules?

what rule have to put to control the elevator with SIGA-CR

Posted: Sat Jan 05, 2013 10:19 am
by abdul wahab
What rule we have to put so as to give elevator the command required to operate in fire alarm condition.
we have installed two SIGA-CR for each elevator
we have two cases, which are something like these

1. in case of fire in all floors (except ground floor) the elevators will come on ground floor
2. in case of fire in ground floor the elevators will come on Basement floor