what rule have to put to control the elevator with SIGA-CR

Post Reply
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Re: what rule have to put to control the elevator with SIGA-

Post by Leo »

Let me know if you need more
---------------------------------------------------------------------
{ ---------- ELEVATOR RECALL ----------- }

[RECALL TO MAIN]
ALARM '*2ND*':
ON NSO '*ELEV_MAIN*';


[RECALL TO MAIN 3RD]
ALARM '*3RD*':
ON NSO '*ELEV_MAIN*';

[RECALL TO ALT]
ALARM '*1ST*':
ON NSO '*ELEV_ALT*';

------------------------------------------------------------------------------

{ ---------- ELEVATOR RECALL ----------- }
[ELEV_UNIT1_MACH_1ST]
ALARM '*ELEV_UNIT1_MACH_1ST*':
ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_ALT',
ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_ALT';

[ELEV_UNIT1_SHAFT_2ND] ALARM '*ELEV_UNIT1_SHAFT_2ND*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_MAIN';
[ELEV_UNIT1_LOBBY_1ST] ALARM '*ELEV_UNIT1_LOBBY_1ST*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_ALT';
[ELEV_UNIT1_LOBBY_2ND] ALARM '*ELEV_UNIT1_LOBBY_2ND*': ON NSO 'RELAY_FREIGHT_UNIT1_ELEV_RECALL_TO_MAIN';

[ELEV_GLASS_LOBBY_1ST] ALARM '*ELEV_GLASS_LOBBY_1ST*': ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_ALT';
[ELEV_GLASS_LOBBY_2ND] ALARM '*ELEV_GLASS_LOBBY_2ND*': ON NSO 'RELAY_GLASS_ELEV_RECALL_TO_MAIN';

[ELEV_MACY_SHAFT-LOBBY_2ND] ALARM '*ELEV_MACY_*_2ND*': ON NSO 'RELAY_FREIGHT_MACY_RECALL_TO_ELEV_MAIN';
[ELEV_MACY_MACHINE-LOBBY_1ST] ALARM '*ELEV_MACY_*_1ST*': ON NSO 'RELAY_FREIGHT_MACY_RECALL_TO_ELEV_ALT';

[ELE_FOOD SHAFT-LOBBY 2ND] ALARM '*ELEV_FOOD_*_2ND*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_MAIN';
[ELEV_FOOD_LOBBY_1ST] ALARM '*ELEV_FOOD_LOBBY_1ST*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_ALT';
[ELEV_FOOD_machine_1ST] ALARM '*ELEV_FOOD_MACH*': ON NSO 'RELAY_FREIGHT_FOOD_RECALL_TO_ELEV_ALT';
Nirujan
Posts: 68
Joined: Thu Sep 26, 2013 8:42 am

Re: what rule have to put to control the elevator with SIGA-

Post by Nirujan »

Is it possible in est3 rules?
abdul wahab
Posts: 1
Joined: Sat Jan 05, 2013 10:03 am

what rule have to put to control the elevator with SIGA-CR

Post by abdul wahab »

What rule we have to put so as to give elevator the command required to operate in fire alarm condition.
we have installed two SIGA-CR for each elevator
we have two cases, which are something like these

1. in case of fire in all floors (except ground floor) the elevators will come on ground floor
2. in case of fire in ground floor the elevators will come on Basement floor