Re: Rules
Posted: Fri Jul 29, 2011 10:14 pm
install 3 other siga-cc1 for confirmation.
[ALARM ZONE 1]
ALARM 'ALM_ZONE_1_*' : ON 'CONF_ZONE_1'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Above False Ceiling
[ALARM ZONE 2]
ALARM 'ALM_ZONE_2_*' : ON 'CONF_ZONE_2'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Below False Ceiling
[ALARM ZONE 3]
ALARM 'ALM_ZONE_3_*' : ON 'CONF_ZONE_3'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Below False Flooring
[ALARM RELEASE 1]
ALARM 'RELEASE_ZONE_1' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
[ALARM RELEASE 2]
ALARM 'RELEASE_ZONE_2' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
[ALARM RELEASE 3]
ALARM 'RELEASE_ZONE_3' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
After create 3 and group with label : RELEASE_ZONE_1, RELEASE_ZONE_2, RELEASE_ZONE_3
activation number 2, activation event Q1 Alarm
in devices select group, add device : CONF_ZONE_1 and clic Q4 and CONF_ZONE_2 and clic Q4 for RELEASE_ZONE_1
made same for other and group with device activation
or for the and group :
RELEASE_ZONE_1 : device : CONF_ZONE_1 and CONF_ZONE_2
RELEASE_ZONE_2 : device : CONF_ZONE_2 and CONF_ZONE_3
RELEASE_ZONE_3 : device : CONF_ZONE_3 and CONF_ZONE_1
[ALARM ZONE 1]
ALARM 'ALM_ZONE_1_*' : ON 'CONF_ZONE_1'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Above False Ceiling
[ALARM ZONE 2]
ALARM 'ALM_ZONE_2_*' : ON 'CONF_ZONE_2'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Below False Ceiling
[ALARM ZONE 3]
ALARM 'ALM_ZONE_3_*' : ON 'CONF_ZONE_3'; {LABEL FOR SIGA-CC1 CONFIRMATION}
...........^==label for Below False Flooring
[ALARM RELEASE 1]
ALARM 'RELEASE_ZONE_1' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
[ALARM RELEASE 2]
ALARM 'RELEASE_ZONE_2' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
[ALARM RELEASE 3]
ALARM 'RELEASE_ZONE_3' : ON -LOW 'RELEASE_GAS', {LABEL FOR SIGA-CC1 RELEASE GAS}
...........^==label for and group
After create 3 and group with label : RELEASE_ZONE_1, RELEASE_ZONE_2, RELEASE_ZONE_3
activation number 2, activation event Q1 Alarm
in devices select group, add device : CONF_ZONE_1 and clic Q4 and CONF_ZONE_2 and clic Q4 for RELEASE_ZONE_1
made same for other and group with device activation
or for the and group :
RELEASE_ZONE_1 : device : CONF_ZONE_1 and CONF_ZONE_2
RELEASE_ZONE_2 : device : CONF_ZONE_2 and CONF_ZONE_3
RELEASE_ZONE_3 : device : CONF_ZONE_3 and CONF_ZONE_1