Hi All
Please help - what does' INT fault' mean with regard to a detector fault on the LCD display - thought it was just tied to on type of detector but have now had the INT fault on another type of detector
adding a isolator base to a balanced map seems to help - comment please
Thanks
EST3 - showing ' INT Fault'
Re: EST3 - showing ' INT Fault'
did you upload the map, the device maybe YELLOW because of the isolator bases
-
- Posts: 2
- Joined: Thu Oct 14, 2010 8:00 pm
Re: EST3 - showing ' INT Fault'
Each detector have 32 code trouble is indicate int. fault on the lcd panel, in 3-sdu software go to signature serie status / diagnotics and clic tab Device Troubles and clic New Data from loop controler for see the internal trouble.
Re: EST3 - showing ' INT Fault'
Hi All and thanks
RE Int faults
These were on multi sensor detectors originally ( has anyone else had faults with them ?) , but recently moved onto optical detectors . ' Using the diagnostics tool '- does this log faults or only see real time ?
Thanks
RE Int faults
These were on multi sensor detectors originally ( has anyone else had faults with them ?) , but recently moved onto optical detectors . ' Using the diagnostics tool '- does this log faults or only see real time ?
Thanks
Re: EST3 - showing ' INT Fault'
Can you provide full pseudo point and ADDRESS Number? If you can, I can identify.
Re: EST3 - showing ' INT Fault'
Siga detectors (I assume 4d?) Or are these Analog addressable detectors? IE--(Wheel address type)??
INT is most likely internal fault. Upload the SIGA Map on Device in question. Is INT device yellow or red like lEO said? What kind of personality code is expected and what is the actual?
If you have "INTERNAL" faults on System sensor type devices, you need to look at program and see what type of smoke is defined in program? What type device is actually out in field? (take down detector in field and look at part #)
Give as much info as possible to us...
Hi All and thanks
RE Int faults
These were on multi sensor detectors originally ( has anyone else had faults with them ?) , but recently moved onto optical detectors . ' Using the diagnostics tool '- does this log faults or only see real time ?
Thanks
INT is most likely internal fault. Upload the SIGA Map on Device in question. Is INT device yellow or red like lEO said? What kind of personality code is expected and what is the actual?
If you have "INTERNAL" faults on System sensor type devices, you need to look at program and see what type of smoke is defined in program? What type device is actually out in field? (take down detector in field and look at part #)
Give as much info as possible to us...