Hi everybody,
I installed RS232 card in J2 slot on CPU card of a EST3 panel and I want to communicate fireworks to panel.also I set port 1 on SDU In Gateway-iii/boudrate 9200 and same setting on system builder.
I have a problem with auxiliary port(auxiliary port1 fault on LCD), and communication fault on Fireworks(System controls).
any one can help me please?
many thanks.
Auxiliary Port fault
Re: Auxiliary Port fault
I suggest to change the baudrate to 19200 , then download the CPU .
Make sure you have the correct COMM port in the device manager in your PC ( if you are using a USB to serial cable which i prefer )
Next step , open system builder update your comm port and baud rate , choose your node , save and exit and it should work.
Please let me know if any further help is required
Make sure you have the correct COMM port in the device manager in your PC ( if you are using a USB to serial cable which i prefer )
Next step , open system builder update your comm port and baud rate , choose your node , save and exit and it should work.
Please let me know if any further help is required