Upgrade IRC3 to IO500 notes

Post Reply
old_tech
Posts: 78
Joined: Wed Jan 23, 2013 7:30 am

Re: Upgrade IRC3 to IO500 notes

Post by old_tech »

Leo wrote:I just upgraded a IRC3 to a IO500.
The main problem was the inability to get the zone descriptions and the 4D map
if the SLC loop is lifted only the first 15 point descriptions are display after that it is only numbers.
Also I was unable to get the point number (zone) and the serial number together,
because of this I needed to find all the siga devices on the SLC loop.


only Siga devices will work on an IO panel
The older system sensor (with addressable wheels) will NOT work on the IO panel, an EST3 system would be needed
That's not a problem, it's a limitation. You'll have to activate each device, 15 at a time, then acknowledge them. if you have 4d loop on screen ,you will see easiest way to approach it.
Leo
Site Admin
Posts: 889
Joined: Thu Dec 11, 2008 7:52 am

Upgrade IRC3 to IO500 notes

Post by Leo »

I just upgraded a IRC3 to a IO500.
The main problem was the inability to get the zone descriptions and the 4D map
if the SLC loop is lifted only the first 15 point descriptions are display after that it is only numbers.
Also I was unable to get the point number (zone) and the serial number together,
because of this I needed to find all the siga devices on the SLC loop.


only Siga devices will work on an IO panel
The older system sensor (with addressable wheels) will NOT work on the IO panel, an EST3 system would be needed
Post Reply