Thanks for replies folks..got issue sorted. The european version of the SSDC card ( SSDC-1E) is not configured to run 24v SMK PWR!!
The older type of cards are.
Search found 5 matches
- Wed Oct 12, 2016 10:00 am
- Forum: EST3
- Topic: Diagnostic faults on SIGA MAB's
- Replies: 8
- Views: 7238
- Tue Jul 19, 2016 6:24 am
- Forum: EST3
- Topic: Diagnostic faults on SIGA MAB's
- Replies: 8
- Views: 7238
Re: Diagnostic faults on SIGA MAB's
The market place description used in the SDU is European
- Wed Jul 13, 2016 6:03 am
- Forum: EST3
- Topic: Diagnostic faults on SIGA MAB's
- Replies: 8
- Views: 7238
Re: Diagnostic faults on SIGA MAB's
Yes the SSDC-1E is used in Europe.
- Wed Jul 06, 2016 8:26 am
- Forum: EST3
- Topic: Diagnostic faults on SIGA MAB's
- Replies: 8
- Views: 7238
Re: Diagnostic faults on SIGA MAB's
Hey, All microcodes look good, 3-CPU 05.20/05.00 3-SSDC1 05.20/05.20 Not sure if its field related now. These did not exist prior to upgrading SSDC card. SMK PWR cable is daisy chained across UIO's with zero volts being measured. Where do you measure voltage on SSDC card if there is only one cable ?
- Fri Jul 01, 2016 5:27 am
- Forum: EST3
- Topic: Diagnostic faults on SIGA MAB's
- Replies: 8
- Views: 7238
Diagnostic faults on SIGA MAB's
Hello, Just registered to this forum today so hello to all you EST techs out there ! Old SSDC card was swapped out and replaced with a SSDC-1E. Download was carried out to card as outlined below. The following 12 diagnostic faults came in on the panel following download which had no existed before:-...